First of all, the amount of freon that comes pre-charged in the condensing unit is only sufficient for a certain length of copper pipe & takes only a certain amount of rise into consideration. There is no way anyone can tell u the precharge is satisfactory without knowing how long ur copper lines are, how much they rise to ur air handler or how many turns the lines make before they get there. I've installed hundreds of units & the odds r that the precharge is not going to be sufficient.
Additionally, 4 hours of vac time means absolutely nothing. You have to pull down to -30 on the compound gage & it has to stay there on its own while the vac pump is off. Not only does this ensure all moisture is removed from the system, but it also ensures moisture can not get back in.
My advice is that if u really want to save money, have someone who knows what they're doing do it. And not just anyone. Talk to their customers first.
Although the work itself is not all that complicated, the knowledge of doing it right is complex enough that even people with a year or two of experience still do it wrong. It is possible to damage the compressor because of install mistakes. The odds r also very good that ur system will be much less efficient, wasting energy & costing u heaps of money in the longhaul. You will void warrenties & u may have a hard time finding a service technician that will even touch it at that point, at least one that will charge anything close to a reasonable price.
You may end up spending $1000+ on top of ur original investment simply because u did not know one of the hundred, stupid little things an experienced tech knows when doing an install like this.